tim morris
- Kentucky
NEC 250.122 reqires ground conductors to be increased in size proportionatly wih phase condutors. I assume the reason for this is to provide the same additional capacity to the ground conductor to allow for voltage drop as you are allowwing for the phase conductors.
The question is if the phase conductors for a 30 ampre 277 volt roadway lighting circuit needed to be #4 wire and the corresponding ground conductor was a #8 to meet the 3% voltage drop limitations, and for other reasons that did not relate to the current or voltage capacity of the conductors(ie the contractor had larger wire available) the phase conductors installed were #1/0, would the ground need to be increased just because a larger than necessary phase coonductor was used?
If the point of the code is to insure all conductors are adequatly sized then as long as the ground is sized for the connected load and length of circuit, the increase in phase conductors is irrevelent. The fact that you can meet all code requirements using the #8 ground if the phase wires are downsized would seem to make this a clear issue.