Here's the scenario.
2500KVA XFMR to 3000A main circuit breaker (MCB). Secondary voltage is 480VAC.
8-750MCM/PH on the secondary in conduit
High Resistance Grounding system employed and wired similar to Exhibit 250.21
Without the HRG (please verify), NEC 250.102(C)(2) indicates that the supply side bonding jumper should be:
#2/0 in each raceway OR
12.5% x 8 x 750MCM or a single 750MCM to bond the eight raceways per NEC Table 250.102(C)(1), note 1
Bonding cable routes from the xfmr XO to the main CB ground bus
With the HRG, there doesn't appear to be a need for a supply side bonding jumper as the XO will not be bonded to ground. Per Exhibit 250.21, it doesn't show a bonding conductor from the transformer to the MCB enclosure, but not certain if this illustration is considered "code".
Does the code require me to run a non-current carrying conductor from the xfmr to MCB?
2500KVA XFMR to 3000A main circuit breaker (MCB). Secondary voltage is 480VAC.
8-750MCM/PH on the secondary in conduit
High Resistance Grounding system employed and wired similar to Exhibit 250.21
Without the HRG (please verify), NEC 250.102(C)(2) indicates that the supply side bonding jumper should be:
#2/0 in each raceway OR
12.5% x 8 x 750MCM or a single 750MCM to bond the eight raceways per NEC Table 250.102(C)(1), note 1
Bonding cable routes from the xfmr XO to the main CB ground bus
With the HRG, there doesn't appear to be a need for a supply side bonding jumper as the XO will not be bonded to ground. Per Exhibit 250.21, it doesn't show a bonding conductor from the transformer to the MCB enclosure, but not certain if this illustration is considered "code".
Does the code require me to run a non-current carrying conductor from the xfmr to MCB?