Re: Grounding Conductor
just 2 cents
If you check the tables in the IAEI adaptation of Soares book on grounding. Tables 11 and 13 suggest that the size of the OCPD and the length and diameter of the raceways; Conduit , and EMT are terminal when employed as an EGC.
For example a run with conductors 12AWG protected at 20A in 1/2 EMT. The maximum length of raceway is indicated as 265 feet.
Yes yes I know rare to exceed that length, but these test were most likely conducted with 26 and 1 /2, lengths of emt. No boxes and maybe set screw connectors.
I'm not an engineer but I do think about this stuff at times.
"Edited for my usual poor grammer"
Charlie