This Project Is Under The 1999 NEC.
I Have A 2500A Double Ended Switchboard With A Full Sized 2500A Tie Breaker.
I Have Run A #6 Copper Wire To A 3/4" x 10' Driven Ground Rod. A #3/0 Copper Wire To The Incoming Water Service. And A #3/0 Wire To The Building Steel.
There Has Been A Claim That The #3/0 To The Water Line Is No Good Because It Does Not Have Contact With At Least 10' Of Earth {1999 NEC 250-50(a)}. Also The Building Steel Is Not Acceptable Because It Is Isolated And Supposedly Not Effectively Grounded {1999 NEC 250-50(b)}.
If All Of The Above Is True Does The Wire To The Driven Ground Rod Need To Be Larger Than #6 Wire {1999 NEC 250-50(a)(2)} (ie Does It Have To Be #3/0 Per Table 250-66)
Also The System Was Tested With A Three Point Fall Of Potential Method And Is Below The 5ohms Required In The Specifications.
Any Help With This Matter Is Appreciated.
-Ed