A while back we changed a service in an old house. The house had a bunch of cloth covered cable where the hot an neutral were #14 and the grounding conductor was #16. With everything going on we didn’t realize that the ground bar was only good for #14 through #4. Would you go back and splice #14 bare to the #16 grounds, or would you leave it alone?
 
I would leave it alone but I'm not saying that is the right thing to do.
 
Even if the hot and neutral were #12 and the ground was #16 I could pigtail the ground with #14 to the bar, correct?
 
A while back we changed a service in an old house. The house had a bunch of cloth covered cable where the hot an neutral were #14 and the grounding conductor was #16. With everything going on we didn’t realize that the ground bar was only good for #14 through #4. Would you go back and splice #14 bare to the #16 grounds, or would you leave it alone?
I think your talking about the service bus grounding bar and old knob and tube wiring which often did not include a EGC ground wires but in your case 16 AWG.

CURRENT CODE is limitex to 14 AWG

SINCE this wiring was proably done before current code, i think you could have just pigtailed a 14 awg in the service panel onto the 16 Awg and terminate in the ground neutral bus bar
 
I think your talking about the service bus grounding bar and old knob and tube wiring which often did not include a EGC ground wires but in your case 16 AWG.
He stated that he has old NM cable no mention of knob and tube which did not have any EGC.
 