Hey gang,
So my question this time is the following:
Suppose you have a feeder made up of 10 sets (EMT conduit), and it was upsized to 10 sets to account for voltage drop. According to NEC section 250.122(B), you have to upsize the equipment grounding conductors also, in proportion to the upsizing of the phase conductors. So now you have upsized equipment grounding conductors inside each set of conduit (EGC's).
1) Let's say you decide NOT to use the grounding conductors, and decide that the EMT metallic enclosure will serve as the grounding.... so you get rid of the EGC's inside the conduits. How does the metallic enclosure / EMT conduits achieve the same effect as the upsized EGC's? is it because we have more surface area with the 10 sets of conduits?
2) Why do you even have to upsize the EGC's (obviously i will anyway since it's required by code), if the metallic conduits can already serve as the path for ground faults? If I have an EGC inside the conduit, wouldn't the ground fault just travel across the EGC and the conduit together?
Just trying to understand the concepts.
So my question this time is the following:
Suppose you have a feeder made up of 10 sets (EMT conduit), and it was upsized to 10 sets to account for voltage drop. According to NEC section 250.122(B), you have to upsize the equipment grounding conductors also, in proportion to the upsizing of the phase conductors. So now you have upsized equipment grounding conductors inside each set of conduit (EGC's).
1) Let's say you decide NOT to use the grounding conductors, and decide that the EMT metallic enclosure will serve as the grounding.... so you get rid of the EGC's inside the conduits. How does the metallic enclosure / EMT conduits achieve the same effect as the upsized EGC's? is it because we have more surface area with the 10 sets of conduits?
2) Why do you even have to upsize the EGC's (obviously i will anyway since it's required by code), if the metallic conduits can already serve as the path for ground faults? If I have an EGC inside the conduit, wouldn't the ground fault just travel across the EGC and the conduit together?
Just trying to understand the concepts.