NOV
Member
- Location
- Upstate NY
- Occupation
- IDC Electrical Review Engineer
I have a situation where an engineer is upsizing a feeder due to voltage drop. Using 75 degree C, the upsized feeder is rated 200A and it is sourced via a 175A breaker. Article 250.122(B) tells me that I have to increase the grounding conductor proportionately according to the circular mil area of the ungrounded conductors. This article is typically pretty straight forward for me but what’s making me doubt the increase in this case is that the upsized feeder (200A - #3/0 ungrounded conductor) and the feeder required for the intended load (175A - #2/0 ungrounded conductor) both use the same size grounding conductor (#6AWG) as shown in Table 250.122. Do I increase the #6AWG grounding conductor by 126% to a #4AWG or is the #6 acceptable in this installation? My initial thought was to increase it but isn’t the reason for the increase of the grounding conductor to handle the additional fault current that the increased ungrounded conductors would allow? The grounding conductor is already rated for the 200A. This one has me a little puzzled.
Thanks in advance!
Thanks in advance!