T transman2 Senior Member Location Brooklet,Ga. Apr 6, 2012 #1 Is it ok to have both at same time. 1. EMT conduit with grounding bushing. 2. Green grounding conductor. Both grounding at same point in panel. Thanks!
Is it ok to have both at same time. 1. EMT conduit with grounding bushing. 2. Green grounding conductor. Both grounding at same point in panel. Thanks!
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 6, 2012 #2 I don't see any problem.
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 6, 2012 #3 In some cases two equipment grounding paths (one being the raceway) are mandatory, see 517.13(A) and (B) Roger
In some cases two equipment grounding paths (one being the raceway) are mandatory, see 517.13(A) and (B) Roger