brian john
Senior Member
- Location
- Leesburg, VA
I have a project, where we did an inspection and now have been asked to work with an electrical contractor in making repairs. here is the problem. There are numerous feeders that are run in the deck (on slab) the conduits are 3" and 3-1/2" ridgid and PVC coated ridgid. Mix and match some are all rigid, others are all PVC coated rigid then some are a combination of both. The were installed with out bushings and there are no threads on either end. In addition there is no bonding of the conduits, they stub out of the deck with no metallic connection. Some of the PVC coated rigid conduits have no continuity to ground.
The conduits need bushings, and this is possible with insuliners, but the bonding is going to be a problem; as some of the conduits are tightly grouped, no way no install a ground clamp on the conduits. Have thought about cadwelding a EGC to the conduit but this will chance damaging the conductors. Any help with this would be appreciated..
The conduits need bushings, and this is possible with insuliners, but the bonding is going to be a problem; as some of the conduits are tightly grouped, no way no install a ground clamp on the conduits. Have thought about cadwelding a EGC to the conduit but this will chance damaging the conductors. Any help with this would be appreciated..