I have a AHJ asking me to jack hammer up 6 inch's of concrete to sleeve it in PVC. My comment was does any one sleeve a ufer ground or a concrete encased electrode. I kindly asked for him to site the code article. No replay as of yet but will let you know. I was not able to find anything in the code that would prohibit the grounding electrode conductor coming through the slab under the panel.
I appreciate you comment
Marc
if the conductor has an outer coating, thhn, thwn, it is allowed. if the conductor is bare copper it will need to be sleeved with pvc where it leaves the slab because of the corrosive nature of air, copper and concrete at the same point. even rigid metal conduit will break down eventually when it exits the concrete
Frank:
Do you have a code section to support that?
just because they are both metals doesn't mean they react the same to a particular agent. There is a reason we galvanize some steel components or use stainless instead of mild steel. Not so common is applications subject to anhydrous ammonia - galvanizing doesn't hold up in that environment, neither does copper. Severe corrosive locations still may use coated rebar because uncoated likely will not last, it may take longer to corrode then if exposed though.if the conductor is bare, and there is no protection where the conductor leaves the pour, I write up the violation under110.11 and 300.6. since there is no air movement in the pour there is no break down of the copper conductor. rerod in the pour lasts forever. .they are both metals. see100.2
if the conductor is bare, and there is no protection where the conductor leaves the pour, I write up the violation under110.11 and 300.6. since there is no air movement in the pour there is no break down of the copper conductor. rerod in the pour lasts forever. .they are both metals. see100.2
He is saying the point of emergence from the concrete is where there is a problem. I do agree 300.6 doesn't apply though. I can see 110.11 applying - but fail to see this being any more deteriorating condition in most applications then a copper wire emerging directly from the soil. Seen a lot of copper water pipe in contact with concrete over the years with no problems. But put a copper pipe in contact with a zinc coated fastener or strap and you have a problem waiting to happen.300.6 does not apply to conductors.
What do you do when the footing crew lays 20' of bare copper wire in the footing trench?
He is saying the point of emergence from the concrete is where there is a problem.
if the conductor has an outer coating, thhn, thwn, it is allowed. if the conductor is bare copper it will need to be sleeved with pvc where it leaves the slab because of the corrosive nature of air, copper and concrete at the same point. even rigid metal conduit will break down eventually when it exits the concrete
So where do you stop? Push the sleeve 6" down, and now the copper/concrete interface is 6" below the rest of the slab. Unless you instruct them to fill the hole with pitch or something you will never get rid of the air-copper-concrete interface.
Only if your concrete slab is more than 6" thick or over a footing that is, otherwise you'd be in the dirt after the 6" sleeve.
JAP>