The reconnection of an equipment grounding conductor (EGC) to earth through a ground rod happens at detatched buildings where the Main Bonding Jumper is not present.
This ground rod isn't going to do much. At 60 Hertz and around 25 Ohms, the amount of current that flows in it into earth, in a fault involving the EGC, will be very small, as the much lower resistance of the EGC will divide most of the current into the EGC.
But if there is a lightning strike, or some other high voltage surge, impedances shift, depending upon voltage and speed, and the ground can become the easy path for that current.