grounding electrode availability

Status
Not open for further replies.

ryan_618

Senior Member
Am i reading this right? 250.50 states that, if available, these shall be used: water pipe, bulding steel, uffer, ring, rod and pipe, plate.

The 99' NEC worded it a bit differently. Are we now REQUIRING a ground rod at each structure, even if the water pipe is not the only electrode? With that in mind, would someone please explain the word "available" to me?!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: grounding electrode availability

Ryan,
If the rod is not installed, it is not available. There is no change in the intent of the section from '99 to '02.
Don
 