At an industrial site a new 480V Switchboard is being installed inside an electrical room. The switchboard is being fed from a 500kVA transformer with a 480V secondary (transformer is not service entrance).
The Switchboard will have a neutral and a Supply Side Bonding Jumper (SSBJ) coming from the transformer with the neutral connected to the neutral bar of the Switchboard and the SSBJ connected to the ground bus.
My question is weather or not the new Switchboard ground bus needs to have a Grounding Electrode Conductor (GEC) connected between the Switchboard ground bus and earth.
Typically In most Industrial settings that I do work in there is a ground grid that encircles the electrical room which consists of ground rods, and 4/0 copper wire which is tied into the foundations rebar at several points and has pigtails which come out of the concrete slab for connection to the ground bus of equipment sitting on the slab at various locations. I have worked on several projects where we have simply replaced equipment in the same location so we were able to disconnect these ground pig tails from the existing equipment and then re-connect them to the new equipment once it was set in the same location.
The issue I'm looking at now is that this new Switchboard is being located in an area of the existing electrical room where there are no ground pig tails and any of the existing ground pig tails sit across the room at other locations.
I'm not sure that these GEC's are required in a case like this but I believe it is always done as "good practice". Does anyone have any recommendations in a case like this on how to tie the new Switchboard into the existing ground grid? Would it be a good or bad idea to run an existing connection from either inside our outside the room to the Switchboard location for connection?
The Switchboard will have a neutral and a Supply Side Bonding Jumper (SSBJ) coming from the transformer with the neutral connected to the neutral bar of the Switchboard and the SSBJ connected to the ground bus.
My question is weather or not the new Switchboard ground bus needs to have a Grounding Electrode Conductor (GEC) connected between the Switchboard ground bus and earth.
Typically In most Industrial settings that I do work in there is a ground grid that encircles the electrical room which consists of ground rods, and 4/0 copper wire which is tied into the foundations rebar at several points and has pigtails which come out of the concrete slab for connection to the ground bus of equipment sitting on the slab at various locations. I have worked on several projects where we have simply replaced equipment in the same location so we were able to disconnect these ground pig tails from the existing equipment and then re-connect them to the new equipment once it was set in the same location.
The issue I'm looking at now is that this new Switchboard is being located in an area of the existing electrical room where there are no ground pig tails and any of the existing ground pig tails sit across the room at other locations.
I'm not sure that these GEC's are required in a case like this but I believe it is always done as "good practice". Does anyone have any recommendations in a case like this on how to tie the new Switchboard into the existing ground grid? Would it be a good or bad idea to run an existing connection from either inside our outside the room to the Switchboard location for connection?