Grounding electrode conductor connection

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have outside feeder fed from another building to the building in below picture.

The outside feeder comes in 200A disconnect outside then feeds the ATS and then panelboard PA with main breaker.

The grounding electrode system is provided at Panel PA. This building is combination of Business B and health care clinics.

I looked at 250.32(B)(1) equipment grounding conductor shall be run with supply conductors and be connected to the building disconnecting means and to the grounding electrodes. Does not say where to connect grounding electrodes conductor to which equipment or maybe it does i am not see it.

Problem is that should the building grounding electrode conductors be connected to 200A disconnect outside or Panelboard PA that has main breaker? Anyone know for sure and where is it in code language

40b2ce8ef1a615a819b1f183b30452f7.jpg
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Problem is that should the building grounding electrode conductors be connected to 200A disconnect outside or Panelboard PA that has main breaker? Anyone know for sure and where is it in code language
The code is silent on this one.
 