W Wire_nutz Member Aug 11, 2010 #1 What are acceptable connectors/fittings and methods for attaching Grounding Electrode Connectors NOT in a raceway to a panel board or a metal box.
What are acceptable connectors/fittings and methods for attaching Grounding Electrode Connectors NOT in a raceway to a panel board or a metal box.
roger Moderator Staff member Location Fl Occupation Retired Electrician Aug 11, 2010 #2 Just run them through the factory supplied 5/16" opening or drill your own. Don't fall for the xxxxx clamp is required BS. Roger
Just run them through the factory supplied 5/16" opening or drill your own. Don't fall for the xxxxx clamp is required BS. Roger
W Wire_nutz Member Aug 11, 2010 #3 roger said: Just run them through the factory supplied 5/16" opening or drill your own. Don't fall for the xxxxx clamp is required BS. Roger Click to expand... Really? No requirement to be securely fastened.
roger said: Just run them through the factory supplied 5/16" opening or drill your own. Don't fall for the xxxxx clamp is required BS. Roger Click to expand... Really? No requirement to be securely fastened.
raider1 Senior Member Staff member Location Logan, Utah Aug 12, 2010 #4 Wire_nutz said: Really? No requirement to be securely fastened. Click to expand... Not to the enclosure where the GEC enters. As Roger stated you can use the small hole provided in the enclosure or drill your own. Chris
Wire_nutz said: Really? No requirement to be securely fastened. Click to expand... Not to the enclosure where the GEC enters. As Roger stated you can use the small hole provided in the enclosure or drill your own. Chris
M macmikeman Senior Member Location Planet macmikeman Aug 13, 2010 #5 I get all choked up whenever the subject of a certain (hint- Loggins and Mesina) _______ clamp comes up....
I get all choked up whenever the subject of a certain (hint- Loggins and Mesina) _______ clamp comes up....