Jps1006
Member
- Location
- Northern IL
I have inherited an installation mess I want to try to correct. Residential 200-amp overhead service with a main breaker is located on the exterior of a garage. The 200-amp feeders run through a slab in PVC with no equipment grounding conductor to the panel in the basement. Currently there is an electrode grounding conductor that goes from the water meter to the panel with the panel bonding screw installed. Clearly this is wrong and the GEC needs to go to the first point of disconnect in the meter and the bonding screw in the panel should be removed. Of course this is all behind drywall in a high end finished basement.
I have a route to get the GEC to the meter using some existing underground PVC, but I will have to pull through the panel.
After I pull out the bonding screw, I'll install a ground buss and move the greens to it. I really don't think I can pull past the 200-amp feeder conductors in the PVC to add an equipment ground for the panel.
Can I pull my #4 GEC and #6 EGC through the same conduit?
I have a route to get the GEC to the meter using some existing underground PVC, but I will have to pull through the panel.
After I pull out the bonding screw, I'll install a ground buss and move the greens to it. I really don't think I can pull past the 200-amp feeder conductors in the PVC to add an equipment ground for the panel.
Can I pull my #4 GEC and #6 EGC through the same conduit?