I just installed a (200A) Main disconnect panel on a pole for a mobile home service.
It sits directly below the meter and is connected to the meter base by PVC conduit.
It's fed by 3 conductor (4/0 Al) USE cable from meter to disconnect.
The main disconnect (metal) enclosure has a aluminum terminal bar that has only 3 lugs, one for the service grounding conductor, one for the GEC, and one for the Grounded feeder conductor to the house.
This bar also has a #10 green (main) bonding screw to bond it and a additional (seperate) equipment grounding bar to the enclosure.
This equipment grounding bar is bolted to the enclosure.
I landed the GEC and the grounded (feeder) conductor on the terminal beside the grounded service conductor, installed the bonding screw, and landed the feeder grounding conductor (to the home) on the seperate (bonded) grounding bar.
I really don't like this set-up, although I believe that I installed it correctly.
I don't like it because the 2/0 Al (feeder) equipment grounding conductor depends on the green #10 bonding screw for it's connection to the service ground.
It seems to me that the GEC should be landed on the equipment ground bar, and the Feeder grounding conductor landed on the same ground bar as the service ground.
This would assure a better grounding connection for the feeder and not depend on the screw for bonding all of the house equipment grounds.
Maybe I'm wrong, but I'd rather have a better (lower impedance)connection for the (feeder) EGC than the Grounding electrode conductor.
This Main breaker panel is a new (for me) brand.
It seems like the NEC places a lot of faith in a #10 screw to provide a sufficient, long lasting bond between the grounded service conductor and the equipment ground.
I know that it's in the code, but it seems kind of weak to me.
Any comments, or suggestions?
steve
ps....I think that the (correct?) answer to the OP's question is "B".