I am in an Electrical Program taking an NEC 1 class and my teacher is no help. I am wanting to check my work to make sure I am on the right track. Below is the question and how I solved it. Can anyone verify if my answer is correct?
A multifamily dwellings service-entrance conductors consist of four paralleled sets of 3/0 AWG THHN copper conductors. What size copper grounding electrode conductor is required?
2/0 AWG
Table 250.66 is used to size grounding electrode conductors for A/C systems. Note 1. States If multiple sets of service-entrance conductors connect directly to a service drop, set of overhead service conductors, set of underground service conductors, or service lateral, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
My understanding of that is that you would add up the areas of the parallel conductors and use the combined area to size your grounding electrode conductor using Table 250.66. Does that sound right? My work is listed below.
(1) 3/0 AWG THHN Copper conductors' area is 167,800 per Table 8, Chapter 9.
167,000 x 4 parallel conductors = 671,200 cmil = 671.2 kcmil
Table 250.66 states Copper conductors Over 600 kcmil through 1100 kcmil requires a 2/0 AWG Copper Grounding Electrode Conductor.
A multifamily dwellings service-entrance conductors consist of four paralleled sets of 3/0 AWG THHN copper conductors. What size copper grounding electrode conductor is required?
2/0 AWG
Table 250.66 is used to size grounding electrode conductors for A/C systems. Note 1. States If multiple sets of service-entrance conductors connect directly to a service drop, set of overhead service conductors, set of underground service conductors, or service lateral, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
My understanding of that is that you would add up the areas of the parallel conductors and use the combined area to size your grounding electrode conductor using Table 250.66. Does that sound right? My work is listed below.
(1) 3/0 AWG THHN Copper conductors' area is 167,800 per Table 8, Chapter 9.
167,000 x 4 parallel conductors = 671,200 cmil = 671.2 kcmil
Table 250.66 states Copper conductors Over 600 kcmil through 1100 kcmil requires a 2/0 AWG Copper Grounding Electrode Conductor.