I'm confused on when a contractor will need to connect an electrode grounding conductor from a sub-panel to ground for panelboards that are NOT the service. When I walk some areas I notice that all panelboards are connected to a grounding bus bar via electrode grounding conductor. Then I walk other areas (usually remote areas not in electrical rooms) where this is not the case. It's confusing on exactly when you should be installing this electrode conductor.
Typically you have an equipment grounding conductor that is installed in all conduit to equipment for bonding. So you are creating an effective ground fault current path with all equipment in the case where there is a ground fault that energizes the case of metallic equipment. This goes to either a transformer (separately derived system) or the service. At the separately derived source (or service) is where the neutral and ground get connected to complete this path and allow for the functioning of breakers to open and clear the fault. Also, at this point is where the bonding jumpers are installed and the electrode ground conductor is connected to building steel, metal water pipe, ground rod, etc.. I don't think you need to install this same electrode grounding conductor to downstream lighting and appliance panelboards. It doesn't quite make sense, other than trying to create a stronger equipotential point. So are these electrode conductors to ground bars installed just for equipotential? If this is required to limit voltage to ground then shouldn't ALL panelboards have this?
Typically you have an equipment grounding conductor that is installed in all conduit to equipment for bonding. So you are creating an effective ground fault current path with all equipment in the case where there is a ground fault that energizes the case of metallic equipment. This goes to either a transformer (separately derived system) or the service. At the separately derived source (or service) is where the neutral and ground get connected to complete this path and allow for the functioning of breakers to open and clear the fault. Also, at this point is where the bonding jumpers are installed and the electrode ground conductor is connected to building steel, metal water pipe, ground rod, etc.. I don't think you need to install this same electrode grounding conductor to downstream lighting and appliance panelboards. It doesn't quite make sense, other than trying to create a stronger equipotential point. So are these electrode conductors to ground bars installed just for equipotential? If this is required to limit voltage to ground then shouldn't ALL panelboards have this?