I have a Transformer feeding a Switchboard with a 4000A3P Main Breaker and 11 sets of parallel conductors at 4#500KCMIL CU conductors.
What is the grounding electrode conductor size that I should use?
Per Table 250.66 of 2011 NEC for 500 KCMIL, I think I need to use 1/0 grounding electrode conductor.
I have a coworker who tells me that it should be 3/0, because having the 11 sets of 500KCMIL puts me far over 1100KCMIL.
I cannot find in the code to prove he is right or wrong. Am I correct or is he correct?
What is the grounding electrode conductor size that I should use?