I've got a customer that just purchased a trailer-mounted generator for use on a construction site to run some equipment. The generator is a 600KW, 3-phase, 4-wire, 480 VAC unit. The generator connections are wired to a circuit breaker (trip unit long-time set to 800A) mounted inside of the generator enclosure. The customer does not have any equipment that will require the neutral. We will be bonding the neutral to the ground in the generator enclosure and then running a grounding electrode conductor to a ground rod.
I know we should size the grounding electrode conductor based on 250.66 but this allows us to use a #6 copper for this purpose (assuming we use a rod electrode and it meets 250.52A(5)). Is that correct?
Also, with regards to the bonding jumper between the Neutral and the ground, it should be sized based on 250.66 as well, right? Since we will have 3 parallel conductors per phase (each is 350 kcmil), this would put the size for the bonding jumper at 2/0 copper. The two parallel conductors would be treated as one 1050 kcmil and thus you'd use that size for table 250.66, right? Thanks in advance.
I know we should size the grounding electrode conductor based on 250.66 but this allows us to use a #6 copper for this purpose (assuming we use a rod electrode and it meets 250.52A(5)). Is that correct?
Also, with regards to the bonding jumper between the Neutral and the ground, it should be sized based on 250.66 as well, right? Since we will have 3 parallel conductors per phase (each is 350 kcmil), this would put the size for the bonding jumper at 2/0 copper. The two parallel conductors would be treated as one 1050 kcmil and thus you'd use that size for table 250.66, right? Thanks in advance.