What size grounding electrode would be required for a 320a meter base 2 200 a panels?
Underground service lateral 400 kcmil copper to meter base 2 sets of 3/0 copper to 2 200a panels? I've always used 2 copper to water main and jumped unbroken from panel to panel.
Was told today 1/0 would be required don't agree due to 250.66 saying based on service enterance conductors not service lateral conductors which would be 2 x 167800 cir miils and 350 kcmils is 350000 cir mills am I missing something? Thanks for any help