Grounding Electrode Conductor?Size

Status
Not open for further replies.

Pistu

New member
250.122 Grounding Electrode Conductor?Size.


Question: What size grounding electrode conductor and how many is required for a 800A breaker that is supplied with

three pvc conduit of 350 kcmil conductors per phase
four pvc conduit of 4/0 kcmil conductors per phase
and etc

to MCC?

Plus, 4/0 Awg underground wire added.

Pistu Papp
 
Pistu said:
250.122 Grounding Electrode Conductor?Size.


Question: What size grounding electrode conductor and how many is required for a 800A breaker that is supplied with

three pvc conduit of 350 kcmil conductors per phase
four pvc conduit of 4/0 kcmil conductors per phase
and etc

to MCC?

Plus, 4/0 Awg underground wire added.

Pistu Papp

250.122 is for equipment grounding conductor. Look in 250.66 and see if that helps
 
First thing is you have got to get the terminology right.

250.122 is about the Equipment Grounding Conductor.

250.66 is about the Grounding Electrode Conductor.


Also are you talking about a service or a feeder?
 
Since it's unlikely that an MCC would be used as a service I would say that these conductors are feeders. Therefore you would use table 250.122. For a 1200 amp feeder that would be a #3/0 cu conductor in each raceway whether you used 3 or 4 conduits based on the 1200 amp OCPD protecting the feeder.
 