I have 3 service switches:
3-Pole 600A, conductors entering are 2 sets of 4#350KCMILS copper
3-Pole 1200A, conductors entering are 3 sets of 4#600KCMILS copper
3-Pole 800A, conductors entering are 2 sets of 4#600KCMILS copper
I want to connect all service switch neutrals to the copper ground bus. The ground bus will also connect to building steel, water main and ground rods.
I sized all my grounding electrode conductors per table 250.66 (see picture).
Basically #2/0 coming out of the 600A switch,
#3/0 coming out of the 1200A switch and
#3/0 coming out of the 800A switch.
Please correct me if I made errors sizing these grounding electrode conductors, not sure if they are oversized or undersized.
What I am not sure about is how to use table 250.66 to size the grounding electrode conductor for the water main, building steel, and ground rod. I am also not sure how to size a ground bus such as thickness and such. Hope someone can explain. Thank you.
3-Pole 600A, conductors entering are 2 sets of 4#350KCMILS copper
3-Pole 1200A, conductors entering are 3 sets of 4#600KCMILS copper
3-Pole 800A, conductors entering are 2 sets of 4#600KCMILS copper
I want to connect all service switch neutrals to the copper ground bus. The ground bus will also connect to building steel, water main and ground rods.
I sized all my grounding electrode conductors per table 250.66 (see picture).
Basically #2/0 coming out of the 600A switch,
#3/0 coming out of the 1200A switch and
#3/0 coming out of the 800A switch.
Please correct me if I made errors sizing these grounding electrode conductors, not sure if they are oversized or undersized.
What I am not sure about is how to use table 250.66 to size the grounding electrode conductor for the water main, building steel, and ground rod. I am also not sure how to size a ground bus such as thickness and such. Hope someone can explain. Thank you.