Hey I had a conversation with a fellow contractor.
We don't understand why you need to size a underground water pipe as per table 250.66. ( residential)
A CEE or Uffer you need not go larger than #4
and a Ground rod no larger than #6.

With so many water lines being switched to plastic after construction why do we still need to size this like that?
If one does a service change they have no Idea what is in the ground.


Just thinking. ( sorry)
 
Hey I had a conversation with a fellow contractor.
We don't understand why you need to size a underground water pipe as per table 250.66. ( residential)
A CEE or Uffer you need not go larger than #4
and a Ground rod no larger than #6.

With so many water lines being switched to plastic after construction why do we still need to size this like that?
If one does a service change they have no Idea what is in the ground.


Just thinking. ( sorry)

Because at one time, long ago, it was very likely that the water piping system had a much lower electrode to earth resistance than even a CEE.
Should the code change just because the world has changed?
 
With so many water lines being switched to plastic after construction why do we still need to size this like that?
If one does a service change they have no Idea what is in the ground.

Most of the water supply lines here even for new construction are 3/4 (copper) has that changed in your area?

I would say you are correct at a service change you could not verify how long the copper line is or if it has been changed underground. Do you see a lot of building water supply being change from copper in your area?
 
Because at one time, long ago, it was very likely that the water piping system had a much lower electrode to earth resistance than even a CEE.
Should the code change just because the world has changed?

But just for the sake of discussion....The grounding electrode's purpose isn't to carry high fault currents right? I mean yes it could in the case of copper ultimately bonding back to the transformer through your neighbors house, but just seems like that's not it's purpose...
 
But just for the sake of discussion....The grounding electrode's purpose isn't to carry high fault currents right? I mean yes it could in the case of copper ultimately bonding back to the transformer through your neighbors house, but just seems like that's not it's purpose...

I think the idea is that they wanted the GEC to hang in there if an service conductor shorted to a service enclosure or the neutral even if the neutral was open at the far end.
 