M mf Member Dec 15, 2004 #1 What is the correct grounding electrode conductor size for a 2000A service that is being fed by 5 sets of 500mcm in pvc. I am talking about the conductor from the MDP to building steel.
What is the correct grounding electrode conductor size for a 2000A service that is being fed by 5 sets of 500mcm in pvc. I am talking about the conductor from the MDP to building steel.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Dec 15, 2004 #2 Re: Grounding Electrode Conductor Sizing 3/0 See 250.56 don