Butler said:I assume this is due the the rods impedance?
haskindm said:The reason that a GEC to a ground rod need not be larger than #6 AWG is because the Ground Rod CANNOT carry fault current. If one leg of a 240-volt service becomes shorted to the GEC and the ground rod has a 25-ohm resistance the GEC will carry 4.8 amps (120/25= 4.8 amps). What purpose would be served by installing a larger GEC?
jwelectric said:Is the rod supposed to carry fault current?
(1) Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.
I was under the impression that the bonding of the equipment grounding conductors and the grounded neutral was for the purpose of clearing a fault.