I have an older Apartment Building that replaced the old water metal main to the building with plastic PEX type waterline. Need to add ground rods as water line was the Grounding Electrode. The building is 2 story 10 unit building with 5 unit flats on each floor. No multi-gang meter banks with disconnects. Each unit has a surface meter with split buss panels in each unit. 5 groups of 2 meters on back wall of building. Each meter has it's own underground Service Lateral feeding each individual meter with each meter feeding each electrical panel. My opinion is we have 10 separate individual Services and I will need to run a separate #6 copper grounding electrode conductor from each Electrical Panel to Ground Rods. My understanding of the NEC article 250 is that i can run a #6 copper or larger out of the farthest electrical panel and run to a pair of ground rods. I believe can the run a #6 copper out of the other 9 Electrical Panels and splice onto the length of G.E.C. running to the ground rods using "Burndy Hyground Compession Grounding Crimps Type YGC" like you would a grounding / bonding grid on a pool? Any opinions?