250.64(D) says it shall be permitted to connect taps from each service panel to a common grounding electrode conductor as illustrated in the handbook.
I'm assuming the common grounding electrode conductor isn't necessary if the taps go directly to building steel. Am I correct?
Sizing of the taps would be based on 250.66 per the service conductors feeding each panel.
Thanks
Buck
I'm assuming the common grounding electrode conductor isn't necessary if the taps go directly to building steel. Am I correct?
Sizing of the taps would be based on 250.66 per the service conductors feeding each panel.
Thanks
Buck