collinkonow
Connecticut E-1 Electrical Contractor
- Location
- Franklin, CT
- Occupation
- Electrician
Is there a specific chapter in the NEC that states that a grounding electrode conductor can't come from the two ground rods, run up the side of the building (protected in conduit) and into the meter enclosure then through the pvc nipple located in the meter enclosure and into the panel? A local building inspector here in Connecticut says that it must not enter the meter enclosure and must pass through a separate hole in the building and then into the panel. Also, if it is allowed to be passed through the meter enclosure must it be bonded to the enclosure even though a pvc nipple is used. I should add that it runs continuous through the enclosure and is not spliced at all. it merely goes from one conduit to another. Thanks in advance for any help and advice.