I'm looking at putting in a 400 amp service. It is a all wood structure. It looks like I'll be using ground rods. Table 250.66 says the grounding electrode conductor will be 3/0 AL.
Since I would be using ground rods I look at 250.66 (A) My question is I don't understand what the code is saying by "...that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than # 4 AL."
Is the code saying the whole conductor can be #4 AL or are they saying to give the 3/0 AL a "haircut" to #4 AL size. Neither seems to me to be right. I must be missing something.