I installed a 400 amp service, on a pole, as a temporary installation for some modular buildings. The only grounding electrode is 2 - 5/8 x 8' rods.
In accordance with article250.66 (A), I ran #6 solid copper as the sole grounding electrode conductor.
I was told that this was unacceptable, and that I should use 2/0, as required by Table 250.66, because although it goes to the rod, it is my primary, (not supplemental), grounding electrode conductor.
My contention is that if the conductor is connected to a rod, regardless of primary or supplemental, it is not required to be larger that #6. The rod is not capable of conducting more that 60 amps.
Am I correct?