Under article 250-66 A if the only source of grounding is a driven ground rod on a residential 200 amp service with 2/0CU entrance conductors can the can the wire to the ground rod be a #6solcu conducter
Yes Roger, after thinking about it I would agree with you. But I'm sure someone will argue that the #6 conductor extending out to the rods isn't run along the building finish. BTW, #6 to the rods is standard here. Never had a inspector question it in 20+ years.It doesn't necessarily have to be protected.
What is the definition of "exposure to physical damage"?
That's good, because the NEC allows it.Originally posted by infinity:
BTW, #6 to the rods is standard here. Never had a inspector question it in 20+ years.
You could run 4 AWG but you do not have to.Originally posted by dillon3c:
If your only source of grounding this 200 ampere residential service,is this one single driven electrode..
You'll need to size the grounding electrode conductor, in Table 250.66
*It will be 4AWG to this driven electrode,not 6AWG in size..
Dillon I have no idea why you think it matters if it is the only electrode or part of a large number of electrodes.Originally posted by dillon3c:
I'm sorry too bob..
This is the only grounding system present..
IMO..it's a common grounding electrode conductor..Table 250.66
But then they run a #6 down the pole. :roll: I don't understand how a pole mounted transformer is any different than a pad mount, and why they require such beefed up grounding for a pad mount.Originally posted by iwire:
That sounds like when we build transformer pads for the power company. They require four 10' x 3/4" rods around the perimeter all connected by 4/0 bare cu.