When a service conductor has been sized for voltage drop do you size the electrode conductor to the bigger size?
Yes.
However, you can reduce the service conductor size say from meter pan to the service disconnecting means (assuming both are in close proximity), and then run a "normal-sized" GEC(s) to the disconnecting means.
I agree that it goes to intent as opposed to literal interpretation.Smart table 250.66 states that we must use the size of the largest service conductor. I don't see how reducing the conductors from the meter to the panel would change that.
I agree. Please make a note of it. :happyyes:...I believe this may need a clarification in 2020.
Smart table 250.66 states that we must use the size of the largest service conductor. I don't see how reducing the conductors from the meter to the panel would change that.
If you run 500 aluminum from transformer to meter socket (long run) and then run 4/0 aluminum from meter socket to 200 amp service disconnecting means inside a house - and land the GEC in the service disconnecting means do you size it for the 500 or the 4/0?
I would size it for the 4/0 service entrance conductor unless someone convinces me it must be sized to the 500 underground service conductor/lateral.