Grounding Electrode Conductor

Status
Not open for further replies.
Effective at anything. If I set a small stepdown transformer 500-600 feet Fromm the building GES, run my GEC back to it, What did it do??

why would you need it anyway? the transformer pad is a structure that needs its own GES. There would need to be either an EGC or a supply side bonding jumper going back to the service depending on where the OCPD is, but not a GEC.
 