I have incoming service into trough. The trough taps to three service disconnects. Two are next to trough however third is fire pump service disconnect/ats/controller located 100 feet away.
The grounding is at trough as per NEC 250.64(D). Service conductors with GEC is routed in conduit within 2 inch concrete encased from trough to the fire pump service disco/ats/controller all in one.
Inspector flagged saying GEC cannot be in same conduit as service conductors.
Can you place grounding electrode conductor in same conduit with service conductors?