250.66(A) States that the portion of the conductor that is the sole connection to the grounding electrode conductor shall not be required to be larger than 6 AWG CU or 4 AWG AL wire.
Does this mean that the GEC attached to the service if not attached to anything else dosn't have to be sized with table 250.66? i.e; 400 AMP residential service with no other means of grounding except the ground rods.