Is there any scenario that would require the grounding electrode conductor to a ground rod to be larger then a number 6?
By code no.Originally posted by george t. everett:
Is there any scenario that would require the grounding electrode conductor to a ground rod to be larger then a number 6?
#4 is one way to eliminate the "follow the contour" requirement. If you don't want to follow the contour with #6 you have to protect it. It may be cheaper or easier to go #4. That was my point.Originally posted by drg:
Wayne,
Using #4 wire would make following a conture harder would it not ??
John
It only mentions #6 so there must be a difference between how we can run #6 vs. #4. The citation implies that where it is not securely fastened, it must be protected. So to run #6 unprotected we need to follow the surface (follow the contour).<snip> A 6 AWG grounding conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection where it is securely fastened to the construction. <snip>
get misinterpreted by literate people?The first sentence of 250.64.(B) blankets the rest of the section.
A grounding electrode conductor or its enclosure shall be securely fastened to the surface on which it is carried.