Trying to figure out a job. It's a 6-family building. 7 meters, 60A subs and one 200a disconnect. I'm thinking #4AWG to the water main and 2 ground rods 6' apart. Do I have to run a separate (#6) wire back to the disconnect? Can I just run it to the water main?
Trying to figure out a job. It's a 6-family building. 7 meters, 60A subs and one 200a disconnect. I'm thinking #4AWG to the water main and 2 ground rods 6' apart. Do I have to run a separate (#6) wire back to the disconnect? Can I just run it to the water main?
Trying to figure out a job. It's a 6-family building. 7 meters, 60A subs and one 200a disconnect. I'm thinking #4AWG to the water main and 2 ground rods 6' apart. Do I have to run a separate (#6) wire back to the disconnect? Can I just run it to the water main?
It's a 6-family building. 7 meters, 60A subs and one 200a disconnect.
If there is 20' or more of rebar in the footing or foundation, 250.50 requires you to use that as a grounding electrode.
As with a single panel, the load OCPD's often add to more than the main. That's a non-issue.Really? I'm sure you've done a load calc, and I don't get into this very much but 60A x 7 = 420A.
As with a single panel, the load OCPD's often add to more than the main. That's a non-issue.
That's why we do load calculations, and not make wild guesses based on circuit ratings.Agreed but less than 30 amp per unit sounds awfully low , dont they have to have at least electric A/c . 2- 20amp kitchen c top . Lights and recepts ?