250.66(A)?
A practice test asks: what size GEC for 3/0 ungrounded service conductor to metal water pipe? answer-4awg cu.
Is this correct? If so, what does pipe mean in 250.66(A)?
Also, when we shifted from primarily using ground rods to primarily bonding to the slab some years ago we continued to use 6cu GEC for 3/0 al 200a services. No one has ever called me out on this, but I'm looking at 250.66(B) and I'm thinking it would require 4 cu GEC. Ideas?