250.66(A)?
A practice test asks: what size GEC for 3/0 ungrounded service conductor to metal water pipe? answer-4awg cu.
Is this correct? If so, what does pipe mean in 250.66(A)?
Also, when we shifted from primarily using ground rods to primarily bonding to the slab some years ago we continued to use 6cu GEC for 3/0 al 200a services. No one has ever called me out on this, but I'm looking at 250.66(B) and I'm thinking it would require 4 cu GEC. Ideas?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
250.66(A)?
A practice test asks: what size GEC for 3/0 ungrounded service conductor to metal water pipe? answer-4awg cu.
Is this correct?
Yes, see Table 250.66
If so, what does pipe mean in 250.66(A)?
It means a driven 3/4" pipe, see 250.52(A)(5)(a)

Also, when we shifted from primarily using ground rods to primarily bonding to the slab some years ago we continued to use 6cu GEC for 3/0 al 200a services. No one has ever called me out on this, but I'm looking at 250.66(B) and I'm thinking it would require 4 cu GEC. Ideas?
Your inspectors should be calling this a violation.

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree with Roger. I would use #4 to the CEE even on a 100 amp service simply because if they ever upgrade to a larger size the wire is appropriately sized.
 

kwired

Electron manager
Location
NE Nebraska
...Also, when we shifted from primarily using ground rods to primarily bonding to the slab some years ago we continued to use 6cu GEC for 3/0 al 200a services. No one has ever called me out on this, but I'm looking at 250.66(B) and I'm thinking it would require 4 cu GEC. Ideas?

#6 Cu GEC is acceptable for 3/0 AL service conductors.

3/0 AL conductors are not acceptable for 200 amps. Even in Table 310.15(B)(6).
 
Yes, see Table 250.66 It means a driven 3/4" pipe, see 250.52(A)(5)(a)

Your inspectors should be calling this a violation.

Roger
Ahhh... metal underground water pipe vs rod and pipe, 250.52(A)(1) and 250.52(A)(5). Although it doesnt say driven I clearly see the distinction.
Soo embarassed about the 6 cu, glad I cleared that up hear where Im somewhat anonymous.
Thanks for the help guys! Will be shure to pick up some #4 bare!
 