Hi All,
I'm working on a project at a hospital where they want to bring in this huge cancer fighting machine. The power feed to the machine will be a 90 amp, 480 volt, 3 phase feeder, with several other 120 volt, 20 amp circuits feeding lights / receptacles / miscellaneous equipment.
The vendor of the machine tells me that I had to make sure the electrical service to the building was not grounded to the cold water pipe... a GEC connection to the cold water pipe would introduce electrolysis, thereby affecting the machine. I verified with the building engineer that the building is in fact connected to the cold water pipe, building steel, and a ground rod... so there are 3 grounding electrodes. According to the vendor, this is still a problem, since the cold water pipe is one of the grounding electrodes.
Question: am I allowed to cut the connection to the cold water pipe, thereby eliminating the problem??? I would assume yes, since the service is grounded to 2 other grounding electrodes... building steel and the ground rod, so there is redundancy. Would the code allow this? I would actually be scared to show something like this on a set of drawings. if cutting the connection to the cold water pipe is not allowed, what other solution is there?
Thanks!
I'm working on a project at a hospital where they want to bring in this huge cancer fighting machine. The power feed to the machine will be a 90 amp, 480 volt, 3 phase feeder, with several other 120 volt, 20 amp circuits feeding lights / receptacles / miscellaneous equipment.
The vendor of the machine tells me that I had to make sure the electrical service to the building was not grounded to the cold water pipe... a GEC connection to the cold water pipe would introduce electrolysis, thereby affecting the machine. I verified with the building engineer that the building is in fact connected to the cold water pipe, building steel, and a ground rod... so there are 3 grounding electrodes. According to the vendor, this is still a problem, since the cold water pipe is one of the grounding electrodes.
Question: am I allowed to cut the connection to the cold water pipe, thereby eliminating the problem??? I would assume yes, since the service is grounded to 2 other grounding electrodes... building steel and the ground rod, so there is redundancy. Would the code allow this? I would actually be scared to show something like this on a set of drawings. if cutting the connection to the cold water pipe is not allowed, what other solution is there?
Thanks!