I need some help with Art. 250.68(A). Is the Acorn clamp( mechanical connection) used to attach the EGC to the rod electrode required to be accessible when the rod is driven into the earth?
I need some help with Art. 250.68(A). Is the Acorn clamp( mechanical connection) used to attach the EGC to the rod electrode required to be accessible when the rod is driven into the earth?
No, 250.68 refers to the connection of the GEC at the service (or sds, etc.) side, not at the electrode side.
You want to refer to 250.70 for connection of the GEC to the electrode. It says ground clamps used on pipes, rods, or other buried electrodes shall be listed for direct soil burial.
250.68 Grounding Electrode Conductor and Bonding Jumper Connection to Grounding Electrodes.
The connection of a grounding electrode conductor at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s), or at a separately derived system and associated bonding jumper(s) shall be made as specified 250.68(A) and (B).
(A) Accessibility. All mechanical elements used to terminate a grounding electrode conductor or bonding jumper to a grounding electrode shall be accessible.
Exception No. 1: An encased or buried connection to a concrete-encased, driven, or buried grounding electrode shall not be required to be accessible.
This is not correct. 250.68 is about connection of the GEC to the electrode, it says so in the title of the section. Further, the text of 250.68 (A) makes it clear that it is talking about the connection to the electrode. It is exception 1 that relaxes this requirement in the case of a rod.