What code prohibits the use of the primary feeder equipment grounding conductor from being used as the grounding electrode for a transformer?
Added to 2011 edition...What code prohibits the use of the primary feeder equipment grounding conductor from being used as the grounding electrode for a transformer?
250.121 Use of Equipment Grounding Conductors. An
equipment grounding conductor shall not be used as a
grounding electrode conductor.
Added to 2011 edition...
I used to look at it that way before 2011... but now you have to consider that an EGC must be run with circuit conductors and a GEC no longer qualifies. If you don't want to run a wire-type EGC, the only option I see now is to run metallic raceway that qualifies as an EGC.But what it doesn't say is that you can't use a grounding electrode conductor for equipment grounding purposes, and I am fairly certain there are other places that specifically allow you to acquire an equipment grounding conductor from a GEC.
I used to look at it that way before 2011... but now you have to consider that an EGC must be run with circuit conductors and a GEC no longer qualifies. If you don't want to run a wire-type EGC, the only option I see now is to run metallic raceway that qualifies as an EGC.
That's pretty much the way I see it, to be compliant. FWIW, I think it's outright idiotic having to do so and am open to other ideas. I haven't looked to see if there is any change in 2014 NEC, but if not, feel free to make a proposal to rescind or modify 250.121 in the 2017 edition...So if I have an isolated well pump in the middle of a field that operates @ 480 volt, and no other electrical equipment, but decided I wanted a 120 volt receptacle for convenience purposes and installed a small transformer for it, I either need to
A- run a GEC from the transformer secondary to the existing grounding electrode system for 480 volt system
B- if I would install another grounding electrode I would still need bonding jumpers to the GE system of the 480 volt system
C- run a GEC with the transformer supply conductors and use a metallic wiring method that itself qualifies as an equipment grounding conductor
D- if the wiring method supplying the transformer does not qualify as an equipment grounding conductor and I want to run the GEC with the supply conductors then I have to install both a EGC and a GEC in the raceway even though they may be the same size and may attach to effectively the same point on both ends.
Many will say that a GEC will always have some current and therefore the EGC would too, creating a violation of 250.6(A).250.12 1 Use of Equipment Grounding Conductors An equipment grounding conductor shall not be used as a grounding
electrode conductor.
Exception: A wire-type equipment grounding conductor installed in compliance with 250.6(A) and the applicable requirements for both the equipment grounding conductor and the grounding electrode conductor in Parts II, III, and VI of this article shall be permitted to serve as both an equipment grounding conductor and a grounding electrode conductor.
The 2014 code really puts it back to the way it was before the 2011 code. You could do it if all of the requirements for both the GEC and EGC were met. Not really as easy as it sounds, but it is possible.
Many will say that a GEC will always have some current and therefore the EGC would too, creating a violation of 250.6(A).
Given that a shared GEC-EGC will not oft be employed in a residential system, with the typical witring methods utilized in commercial, institution, and industrial environs, it is next to impossible to isolate EGC current, of any kind, from bonded non-current carrying metal parts or through concrete (especially damp and metal reinforced)... and this current actually returns to the source through the GEC... and vice versa if the connected system is not the source. This is likely the main reason why the NEC does not define objectionable current... and those that say there should never be any current on an EGC, other than fault current, do not truly understand the finer points a grounded-conductor system.Although Mike Holt teaches that the ideal is that there should only be one point of connection between the EGC "network" and the GES "network", there is nothing in the NEC that requires that. If there is current in an EGC whose source is not part of the building wiring system (e.g. earth potential gradients) I do not necessarily see that as objectionable current from the point of view of the NEC. If it does constitute objectionable current, then the only safe and practical solution (other than eliminating the source) is to never share a conductor as EGC and GEC and never to bond any EGC to ground anywhere except at the main bonding point. Given that a lot of electrical equipment can have an incidental earth connection via gas or water pipe or mounting on concrete, the latter may not even be possible.
Just want to add, if there is any objectionable current between terminations, it will be carried by both the EGC and GEC when separate. Under 250.6(B), you'd be permitted to discontinue one or more grounding connections, interrupt the continuity of a conductive path, etc. So technically, one conductor serving both GEC and EGC functions would be the best remedial action anyway.
I still think 250.121 is outright idiotic no matter how much they modify it. :slaphead::happyyes::happyno:hmy:
Which is of dubious value given that all electrodes other than auxiliary electrodes must be bonded together to form a single GES.In the common case where 250.6 applies, the EGC must be run to the source breaker grounding busbar regardless of how noisy or how many amps are found flowing on the other nearby EGC's and their conduits. The GEC however can be run, and imo is required to be run, to a grounding electrode that is "nearby", "accessible", "in contact with the earth", and imo free of objectionable current found elsewhere in the building, especially away from dual fed switchgear and large UPS, VFD's that may have their filter cap sections internally Y connected and grounded (introducing objectionable current that may flow on the grounding paths).
Which is of dubious value given that all electrodes other than auxiliary electrodes must be bonded together to form a single GES.
And that's not a problem where they run essentially different routes... but what about when they run the exact same route and are essentially connected at both ends. I would call that paralleled typically, but that doesn't even meet the requirements of parallel conductors, as the GEC will likely be larger than a wire-type EGC. If a line to ground fault where to occur, more of the fault current would be handled by the GEC in this case, which is exactly the opposite of either's purpose.I think what they may have meant to say is that you have to have a a wire type GEC that is separate from whatever EGC you might have.
250.121 Use of Equipment Grounding Conductors. An
equipment grounding conductor may be used as a grounding
electrode conductor only where all requirements are met for
both conductor types.
250.121 Use of Equipment Grounding Conductors. A
grounding electrode conductor may be used as an equipment
grounding conductor only where all requirements are met for
both conductor types.
Many will say that a GEC will always have some current and therefore the EGC would too, creating a violation of 250.6(A).