RickyBobby
Member
- Location
- Colorado Springs, Co
I recently moved a 300kva XFMR from the 2nd floor, of a office building, to the first floor, because a dentist complained that it was too loud. I ran the 3/0 GE to a 2" water line just outside the electric room above a grid ceiling. The inspector failed me, saying, I need to run the GE within 5' of the point of entry and I need to run a jumper from the 1st floor water line to the 2nd floor water line. I sighted 250.68(c) exception and he said its above a ceiling and not "exposed" (Art. 100 definitions; Exposed (as applied to wiring methods) ...or behind panels designed to allow access), He said this is not wiring methods. Than he stated 250.104(d)(1), "in the area served by..." so I need to take GE to the second floor as well. This came from the senior electrical inspector at the Pikes Peak Regional Building Dept.