Question on how to effectively install a grounding electrode conductor on the secondary side of a step-down transformer:
We have a couple of 480//120/208V transformers to install in a new building; each trasformer is in a different part of the building. The primary feeders to each will be run in PVC underground. The building steel consists only of bar joists on masonry walls; these joists are not effectively bonded together. The main water service is about 150 feet away from each transformer.
The local inspector is requiring a separate ground wire to be installed outside of each conduit in the dirt, to be run from the secondary side of the transformer to the main incoming water line.
This sounds like overkill to me, but as I research the code it appears to be correct.
Any other suggestions?
Thanks
We have a couple of 480//120/208V transformers to install in a new building; each trasformer is in a different part of the building. The primary feeders to each will be run in PVC underground. The building steel consists only of bar joists on masonry walls; these joists are not effectively bonded together. The main water service is about 150 feet away from each transformer.