chris huckins
Member
- Location
- collinsville,il
Having a disagreement concerning installation of GEC. I know 250.119 covers identification of EGC, but I do not see any identification requirements (green) in 250.64 for the GEC, are there any identification requirements for the GEC? Also just looking for some confirmation; the way i see it, 250.64 (B) says that FMC can't be used to protect the GEC from physical damage. To help confirm this 348.12 (7) says FMC is not permitted to be used " where subject to physical damage". So it is a violation to use a short section of FMC from a transformer, for vibration purposes, per 250.64(B)?