Grounding Electrode Not Required?

Status
Not open for further replies.

Trey4U

Member
Location
Alabama
Occupation
Retired Electrical Contractor
The exception to 250.32A says ?A grounding electrode shall not be required when a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non-current-carrying metal parts of equipment?.

I have a structure that has ten single phase MLO panels each with two 30/2 breakers for 20 clothes dryers. Each panel has a multiwire branch circuit going to a distribution panel remote from the structure. Since there are ten multiwire branch circuits wouldn't the exception not apply and a grounding electrode be required for each panel?
 

iwire

Moderator
Staff member
Location
Massachusetts
Each panel has a multiwire branch circuit going to a distribution panel remote from the structure.

Seeing as these circuits sound like they supply a panel they are feeders so the exception does not apply regardless of the number.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have a structure that has ten single phase MLO panels each with two 30/2 breakers for 20 clothes dryers. Each panel has a multiwire branch circuit going to a distribution panel remote from the structure. Since there are ten multiwire branch circuits wouldn't the exception not apply and a grounding electrode be required for each panel?

A separate structure is not permitted to be supplied by 10 different branch circuits unless it meets the conditions in 225.30(A) which your installation does not.
 