richwaskowitz
Senior Member
- Location
- Shelby Twp. MI, near Detroit
Do I understand UL 508A 16.2 correctly in that when an industrial control panel has a control transformer larger than 1000 va, that in addition to the ECG coming in with the supply conductors, a grounding electrode or electrode system will be required to be connected to the panel (for the purposes of bonding the secondary of the transformer)? Meaning that simply installing a bonding jumper from the grounded leg of the transformer secondary to the panel ground bar is not sufficient? I believe it, I am just having a difficult time explaining why this is necessary to those who are arguing that the equipment grounding conductor should be able to serve that function. If my understanding is correct, can anyone explain the reasoning behind this requirement?