Grounding electrode requirements at site light poles

Status
Not open for further replies.

rlqdot

Member
Location
St. Louis, MO - USA
Occupation
Professional Engineer (multiple states) - building design
An inspector on one of my projects in California has told the contractor that he must bond the steel site light poles to the re-bar in the pole base. The contractor has installed a #8 copper wire bonded to the re-bar and intends to land that wire on the pole lug once the pole is installed. The pole (and the luminaire mounted on it) is served by a 208V-1P-20A branch circuit with EGC extended as a part of the branch circuit. It is my position that based on NEC 2011 article 250.32(A) Exception, bonding the pole to the re-bar is not required. It is also my contention that the anchor bolts provide a path to earth - just the same as anchor bolts in a structural steel building as spelled out in NEC 2011 article 250.52(A)(2)(2) so a separate copper wire bond is not required.

Any feedback would be appreciated.
 
An inspector on one of my projects in California has told the contractor that he must bond the steel site light poles to the re-bar in the pole base. The contractor has installed a #8 copper wire bonded to the re-bar and intends to land that wire on the pole lug once the pole is installed. The pole (and the luminaire mounted on it) is served by a 208V-1P-20A branch circuit with EGC extended as a part of the branch circuit. It is my position that based on NEC 2011 article 250.32(A) Exception, bonding the pole to the re-bar is not required. It is also my contention that the anchor bolts provide a path to earth - just the same as anchor bolts in a structural steel building as spelled out in NEC 2011 article 250.52(A)(2)(2) so a separate copper wire bond is not required.

Any feedback would be appreciated.

I think you are correct.

I think the idea of using the rebar in the base as a GE is dubious. Take a look at what the code says can be used as a GE and see if there is anyway it could qualify.
 
I have a study that shows the reinforcing steel in a concrete pole base makes a pretty good ground. I don't have the study readily available but will try to dig it out.
 
On a rescent job we had a ground rod in the base going to rebar in the base going to anchor bolt for light pole and ending at lug in pole. This was specified on plans.
 
new code

new code

An inspector on one of my projects in California has told the contractor that he must bond the steel site light poles to the re-bar in the pole base. The contractor has installed a #8 copper wire bonded to the re-bar and intends to land that wire on the pole lug once the pole is installed. The pole (and the luminaire mounted on it) is served by a 208V-1P-20A branch circuit with EGC extended as a part of the branch circuit. It is my position that based on NEC 2011 article 250.32(A) Exception, bonding the pole to the re-bar is not required. It is also my contention that the anchor bolts provide a path to earth - just the same as anchor bolts in a structural steel building as spelled out in NEC 2011 article 250.52(A)(2)(2) so a separate copper wire bond is not required.

Any feedback would be appreciated.

Auxiliary Ufer?:slaphead:
 