D dvcraven052256 Member Location St. Louis, missouri Occupation Electrical Engineer Aug 26, 2024 #1 I have a 1600 amp service. If connection is to a ground rod only does the GEC required to sized per 250.66 and not #6 cu. as permitted if connecting to rod or pipe.
I have a 1600 amp service. If connection is to a ground rod only does the GEC required to sized per 250.66 and not #6 cu. as permitted if connecting to rod or pipe.
Johnhall30 Senior Member Location New Orleans, LA Occupation Engineer Aug 26, 2024 #2 Ground rod only needs #6, any other electrode needs to be sized per 250.66
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Aug 26, 2024 #3 The GEC to a rod or other made electrode need not be larger than #6 cu.
D dvcraven052256 Member Location St. Louis, missouri Occupation Electrical Engineer Aug 26, 2024 #4 Thx for the quick responses!